Any furnace guys here? won't fire with cover on. Lol wtf

OP
OP
FreePenguin

FreePenguin

Well-Known Member
Joined
Sep 29, 2019
Threads
81
Messages
5,392
Reaction score
3,707
Location
Ohio
First Name
Donald
Vehicle(s)
17 mustang
Vehicle Showcase
1
The vents are clear, both exhaust and intake. I double checked, sucking air with shop vac it’s free flowing on other side.

brand new air filter, I even removed air filter to test.
So a switch or blower is my culprit from reading

costly?
I don’t know what it means to close a switch. But I read ruud or any company, it’s doing a prsssure check and failing

when it’s opened. The pressure check is functioning

94D530BE-F1DF-4C90-B9BC-899E4DDF772C.png
Sponsored

 

BrianH87

Well-Known Member
Joined
May 6, 2018
Threads
13
Messages
382
Reaction score
228
Location
Pittsburgh, PA
Vehicle(s)
2020 Mustang GT ; 2021 Explorer ST
From the sounds of all this, you may need to get someone to check it out. More than likely the pressure switch is the culprit. Or something more serious such as a clogged secondary heat exchanger. Honestly, the blower and filter don't have much to do with any of this. If it was the high temp limit, then yes. But not the pressure switch. That is, unless you have a hole in the heat exchanger or something crazy, which I doubt. But I've seen a lot over the years. Expect the unexpected.

Don't let them try to sell you a new furnace. Lots of Residential outfits push for that because they make more money selling new equipment vs repairing old. And if something doesn't seem right, get a second opinion. Let me know if you have any questions about what they say.
 
OP
OP
FreePenguin

FreePenguin

Well-Known Member
Joined
Sep 29, 2019
Threads
81
Messages
5,392
Reaction score
3,707
Location
Ohio
First Name
Donald
Vehicle(s)
17 mustang
Vehicle Showcase
1
I paid a guy after I went through everything over and out

hecharged $50 to inspect he put blame on the pressure switches, taught me a bit about it.

After he left I saw the smallest darn crack on redsilicone hose connected to the pressure switch
I called local place asked if I can buy silicone hose they told me no.
Said I have to be licensed to buy a small hose

wtf?

went to aurozone. 1.99 vacuum hose.

she works perfect. I guess somehow the hose threw off the pressure. It’s weird by opening the vent it equalized the pressure. No clue

but she works now fully sealed

total spent
50 for guy to look- but he didn’t find the issue. He was actually trying to blame heat exchanger lol. And motherboard. Whstdger

2 dollar kit kat
2 dollar hose

he actually broke the little clip off the wire that clipped to pressure switch, he clamped a new one on and put some electrical tape around it, meh whatever it works.

483E3CCE-B930-4314-BA1D-30C20B6A4A3B.jpeg
 

key01

Well-Known Member
Joined
Nov 10, 2017
Threads
9
Messages
1,411
Reaction score
1,356
Location
Chicagoland
Vehicle(s)
2017 GT350 now gone to a great home.
Glad you got it fixed. Trying to figure out why your intake and exhaust pipes are connected at the wall in that larger pipe. Usually these run to the outside individually. Just curious. Perhaps that through-wall pipe is chambered?
Okay, I researched and it is a concentric pipe. I been schooled.
 
Last edited:
OP
OP
FreePenguin

FreePenguin

Well-Known Member
Joined
Sep 29, 2019
Threads
81
Messages
5,392
Reaction score
3,707
Location
Ohio
First Name
Donald
Vehicle(s)
17 mustang
Vehicle Showcase
1
So furnace has been fine for a week, fires up on own and everything. Now periodically I hear it taking a few times to ignite. Like knock knock knock then tries again and ignites.

One morning, it had locked itself out for an hour I went down saw 1 blink, which says hour lockout.

now I do recall it doing the knock here and there over last few yeara.

should I book a repair diagnoses or should I pay for a tune up? Diagnose is 89, andtune up is 119.

but it doesn’t do knocking everytime so I’m thinking a tune up maybe needed and should fix that

I’m not sure if inspection is same as tune up. But the special is “furnace inspection,$119”
 
Last edited:

Sponsored

Rapid Red

Well-Known Member
Joined
Nov 4, 2019
Threads
45
Messages
5,075
Reaction score
4,097
Location
Woodstock GA
First Name
Greg
Vehicle(s)
GT PP2 RaceRed Roush> Steeda> preformance
Vehicle Showcase
2
I paid a guy after I went through everything over and out

hecharged $50 to inspect he put blame on the pressure switches, taught me a bit about it.

After he left I saw the smallest darn crack on redsilicone hose connected to the pressure switch
I called local place asked if I can buy silicone hose they told me no.
Said I have to be licensed to buy a small hose

wtf?

went to aurozone. 1.99 vacuum hose.

she works perfect. I guess somehow the hose threw off the pressure. It’s weird by opening the vent it equalized the pressure. No clue

but she works now fully sealed

total spent
50 for guy to look- but he didn’t find the issue. He was actually trying to blame heat exchanger lol. And motherboard. Whstdger

2 dollar kit kat
2 dollar hose

he actually broke the little clip off the wire that clipped to pressure switch, he clamped a new one on and put some electrical tape around it, meh whatever it works.

483E3CCE-B930-4314-BA1D-30C20B6A4A3B.jpeg

I can see that a cracked hose being the bad actor. Good find.
BTW we all know hoses are really really hight tech components that only a licensed professional could even possibly think about replacing.

What crap, anyway heat is good, was just thinking about this post the other day......... warm house cold beer LOL

Cheers
 

Interceptor

Daily Driver
Joined
Apr 3, 2018
Threads
69
Messages
1,627
Reaction score
1,213
Location
Low country South Carolina
Vehicle(s)
2019 California Special A10
Not even close to know what I'm talking about but sounds like dust/ residues somewhere
 
OP
OP
FreePenguin

FreePenguin

Well-Known Member
Joined
Sep 29, 2019
Threads
81
Messages
5,392
Reaction score
3,707
Location
Ohio
First Name
Donald
Vehicle(s)
17 mustang
Vehicle Showcase
1
Not even close to know what I'm talking about but sounds like dust/ residues somewhere
I went ahead called the company, 120 is tune up. Said they are sending a senior tech too as well to look for issues while tuning up.

So 30 bucks more than a diagnose/trip I’m getting a full cleaning/inspection/lube.
Just for piece of mind. I’ve been here 5 years and done nothing but change filter and replace that hose

he’s prob going to comment on my hose maybe he has some on his truck
 

mindo389

Well-Known Member
Joined
Nov 28, 2019
Threads
7
Messages
263
Reaction score
308
Location
Baton Rouge, Louisiana
First Name
Charles
Vehicle(s)
2015 Mustang GT 5.0 50th AY Appearance Pkg.
Vehicle Showcase
1
My field is in industrial, however a rubber or plastic hose doesn't make much difference to a pressure switch, as long as it fits snug on the connector. Just like a fuel line or vacuum hose on your car. Your unit does not look old, so I would not replace it, unless your heat exchanger is cracked and carbon monoxide is detected from your registers. Sometimes the control boards fault and can be expensive to replace. Then it is a toss up as to replace the unit or the board. Seems that your unit issue may have been the hose, given that the unit is working after you replaced it. I suspect the switch has dust in it or it is on the verge of failure. I didn't see if you left the access panel loose after you replaced the hose. Interested in what the technician comes up with...
 
OP
OP
FreePenguin

FreePenguin

Well-Known Member
Joined
Sep 29, 2019
Threads
81
Messages
5,392
Reaction score
3,707
Location
Ohio
First Name
Donald
Vehicle(s)
17 mustang
Vehicle Showcase
1
My field is in industrial, however a rubber or plastic hose doesn't make much difference to a pressure switch, as long as it fits snug on the connector. Just like a fuel line or vacuum hose on your car. Your unit does not look old, so I would not replace it, unless your heat exchanger is cracked and carbon monoxide is detected from your registers. Sometimes the control boards fault and can be expensive to replace. Then it is a toss up as to replace the unit or the board. Seems that your unit issue may have been the hose, given that the unit is working after you replaced it. I suspect the switch has dust in it or it is on the verge of failure. I didn't see if you left the access panel loose after you replaced the hose. Interested in what the technician comes up with...
after I replaced the hose, I 100%tightened panel up. And it’s working fine since.

the issue now is periodically it makes the knock noise(gas valves) failure to ignite each attempt. Like occasionally it will require 2nd or 3rd attempt to fire.

it works though, so I’m hoping the tune up will get it all running up to par. Butyeah, the hose did fix the initial issue of not running.
Just want it to run its best now for many more years to come as it runs and heats beautiful. Just need it to do it everytime
 

Sponsored

key01

Well-Known Member
Joined
Nov 10, 2017
Threads
9
Messages
1,411
Reaction score
1,356
Location
Chicagoland
Vehicle(s)
2017 GT350 now gone to a great home.
I pay for spring and fall checkups with a neighborhood contractor and it's only $200 for the year, which includes new humidifier pads and other items. They will then come out 24/7 for no extra charge if something goes haywire. I moved into this house with a 12 year old furnace 3 years ago and have been nursing it along. They have replaced a few cheap components along the way that keep it running efficiently. Your guys may find some things that don't test out and are causing the delayed start. Hopefully, it is all easy and cheap. I'm not replacing my furnace and A/C until it croaks.
 

DCShelby

Well-Known Member
Joined
Jan 24, 2019
Threads
17
Messages
1,131
Reaction score
839
Location
DC
First Name
Robert
Vehicle(s)
2018 GT350 Lighting Blue and 2017 Ducati 1299S
My propane valve was bad, it was stuck closed. When it got a signal to open and flow the gas...the ignition was on but no heat and it switched off and blew a 5 amp fuse on a furnace control board. I had to get a new valve put in and it worked.
 
OP
OP
FreePenguin

FreePenguin

Well-Known Member
Joined
Sep 29, 2019
Threads
81
Messages
5,392
Reaction score
3,707
Location
Ohio
First Name
Donald
Vehicle(s)
17 mustang
Vehicle Showcase
1
Last update, paid mcafee to come out, the guy was senior tech he actually used to be the person who serviced it before I bought house 4-5 years ago. I paid $120 he spent a whole hour plus cleaning it all out, looking at everything. He found a couple small things like an insulator or something was grounding, fixed and cleaned valves and igniter stuff. He found in the intake a shit ton of spider webs, even though my shop vac pulled air, he showed me them, we cleaned it all out.

running. Like a damn champ! He said the vacuum hose I put on there was just fine, he left it. Said it’s really not much different from their hose they use.

Anyway it runs everytime; hasn’t made the clunk fail to ignite noise (even though it wasn’t common) he said it being grounding like that can cause intermittent failure to spark or ark or something.

He also said my heat exchanger looks pretty healthy, my furnace was installed 07, but says my furnace in his opinion from ruud was one of their best furnaces and last well beyond the typical servicing typically seen. He said I very well could get another 5-10 more years.

I asked him about the yearly plan, he said do what I’m doing just pay the turn up every couple yearsusually saves $ in long run vs maintenance everyyear in a monthly installment.

that was his suggestion as my furnaceis healthy

I’m on iPhone and sorry for typo errors. Blower motor was installed in 15-16 by him lol
 

Rapid Red

Well-Known Member
Joined
Nov 4, 2019
Threads
45
Messages
5,075
Reaction score
4,097
Location
Woodstock GA
First Name
Greg
Vehicle(s)
GT PP2 RaceRed Roush> Steeda> preformance
Vehicle Showcase
2
Heat is good, that was a good tune up....
 

key01

Well-Known Member
Joined
Nov 10, 2017
Threads
9
Messages
1,411
Reaction score
1,356
Location
Chicagoland
Vehicle(s)
2017 GT350 now gone to a great home.
Nice. I had two Ruuds in my last home. They make great furnaces. Hope it lasts a long time.